 This is old but should help.
 CLP name was UPSMONITOR.

---
Doug Hart





PGM
/**/
/*                 UNINTERRUPTIBLE POWER SUPPLY MONITOR              */
/**/
/*********************************************************************/
/*                                                                   */
/*          MOBIL CHEMICAL COMPANY PROGRAM MODIFICATION LOG          */
/*          -----------------------------------------------          */
/*                                                                   */
/*   DATE     PGMR  SPR#      DESCRIPTION OF MODIFICATION            */
/* --------   ----  ----   ---------------------------------         */
/*                                                                   */
/* 06/29/90   DIV   0000   PROGRAM CREATED.                          */
/*                                                                   */
/*                                                                   */
/*                                                                   */
/*                                                                   */
/*********************************************************************/
/**/
/*********************************************************************/
/*                                                                   */
/*          WARNING TO PROGRAMMER                                    */
/*          ---------------------                                    */
/*                                                                   */
/*   THIS PROGRAM MUST BE COMPILED WITH THE FOLLOWING OPTION:        */
/*                                                                   */
/*          USRPRF(*OWNER)                                           */
/*                                                                   */
/*   THE UPS MONITOR PROGRAM EXPECTS THE FOLLOWING SYSTEM VALUES     */
/*   IN ORDER TO OPERATE CORRECTLY:                                  */
/*                                                                   */
/*          QUPSMSGQ    =  QUSRSYS / UPSMSGQ                         */
/*          QUPSDLYTIM  =  *NOMAX                                    */
/*          QPWRRSTIPL  =  '1'                                       */
/*                                                                   */
/*   THIS JOB RUNS IN THE CONTROLLING SUBSYSTEM.                     */
/*                                                                   */
/*   SUBSYSTEM CTL01 JOBQ QCTL ALLOWS *NOMAX JOBS, HOWEVER           */
/*   THIS UPS MONITOR PROGRAM ALLOWS ONLY ONE.  ATTEMPTS TO START    */
/*   DUPLICATE UPS MONITOR JOBS WILL BE ENDED AUTOMATICALLY.         */
/*                                                                   */
/*********************************************************************/
/**/
             DCL        VAR(&JOB) TYPE(*CHAR) LEN(10)
             DCL        VAR(&USER) TYPE(*CHAR) LEN(10)
             DCL        VAR(&JOBNUMBER) TYPE(*CHAR) LEN(6)
/**/
             DCL        VAR(&UPSMSGQLIB) TYPE(*CHAR) LEN(20)
             DCL        VAR(&UPSMSGQ) TYPE(*CHAR) LEN(10)
             DCL        VAR(&UPSLIB) TYPE(*CHAR) LEN(10)
/**/
             DCL        VAR(&MSGID) TYPE(*CHAR) LEN(7)
/**/
             DCL        VAR(&JOBCNLREQ) TYPE(*CHAR) LEN(1)
             DCL        VAR(&TENSECOUNT) TYPE(*DEC) LEN(5) /* Ten +
                          Second Power Failure Loop Counter. */
             DCL        VAR(&WAITSEC) TYPE(*DEC) LEN(5 0) /* Declare +
                          Variable For The Time The System Should +
                          Wait Before Beginning Power Down. */
             DCL        VAR(&AWAITSEC) TYPE(*CHAR) LEN(5) /* Declare +
                          Alpha Version Of &WAITMIN. */
             DCL        VAR(&WAITCYCLES) TYPE(*DEC) LEN(5) /* Declare +
                          Variable For Number Of Wait Cycles Which +
                          Must Occur Before System Is Powered Down. */
             DCL        VAR(&MCCCUSMSG) TYPE(*CHAR) LEN(50) /* +
                          Declare Variable For Mobil Customized +
                          Message To Users. */
/**/
             DCL        VAR(&LOOP_LABEL) TYPE(*CHAR) LEN(10)
/**/
             DCLF       FILE(MTXTSRC) /* Declare Mobil Controlled +
                          Source File. */
/**/
/*********************************************************************/
/**/
 SETUP_JOB:
/**/
             RTVJOBA    JOB(&JOB) USER(&USER) NBR(&JOBNUMBER) /* +
                          Retrieve This Job's Attributes. */
/**/
/************CHGJOB*****LOG(4 00 *SECLVL) LOGCLPGM(*YES)*************/
             CHGJOB     RUNPTY(5)
/**/
             OVRDBF     FILE(MTXTSRC) MBR(UPSMONITOR) SECURE(*YES) +
                          /* Override To Member UPSMONITOR In +
                          MTXTSRC File. */
/**/
 NEXRCD:
/**/
             RCVF       /* Read Outfile. */
/**/
             MONMSG     MSGID(CPF0864) EXEC(GOTO CMDLBL(UPDVAR)) /* +
                          If End-Of-File Reached, Update User +
                          Controlled Variables. */
/**/
             GOTO       CMDLBL(NEXRCD) /* Read All Records Until +
                          End-Of-File. */
/**/
 UPDVAR:
/**/
             CHGVAR     VAR(&WAITSEC) VALUE(%SUBSTRING(&SRCDTA 1 5))
             CHGVAR     VAR(&MCCCUSMSG) VALUE(%SUBSTRING(&SRCDTA 10 +
                          50))
/**/
             IF         COND(&WAITSEC <= 00000) THEN(CHGVAR +
                          VAR(&WAITSEC) VALUE(00180)) /* If Value Is +
                          Not Valid, Substitute 180 Seconds. */
/**/
             CHGVAR     VAR(&WAITCYCLES) VALUE(&WAITSEC / 10)
/**/
             CHGVAR     VAR(&AWAITSEC) VALUE(&WAITSEC)
/**/
/*********************************************************************/
/**/
 CHECK_MSGQ:
/**/
             RTVSYSVAL  SYSVAL(QUPSMSGQ) RTNVAR(&UPSMSGQLIB) /* +
                          Retrieve UPS Message Queue Value. */
/**/
             CHGVAR     VAR(&UPSMSGQ) VALUE(%SUBSTRING(&UPSMSGQLIB 1 +
                          10))
             CHGVAR     VAR(&UPSLIB) VALUE(%SUBSTRING(&UPSMSGQLIB 11 +
                          10)) /* Break UPS Message Queue System +
                          Value Into Two Variables. */
/**/
             CHKOBJ     OBJ(&UPSLIB/&UPSMSGQ) OBJTYPE(*MSGQ) /* +
                          Verify That UPS Message Queue Exist. */
             MONMSG     MSGID(CPF9801) EXEC(DO)
/**/
             SNDPGMMSG  MSG('WARNING -- Job ' || &JOBNUMBER |< '/' || +
                          &USER |< '/' || &JOB |< ' has found +
                          Uninterruptible Power Supply *MSGQ ' || +
                          &UPSLIB |< '/' || &UPSMSGQ |< ' missing.  +
                          If system has been recently reloaded, this +
                          condition is normal.  Since this *MSGQ is +
                          always allocated by the UPS monitor job, it +
                          can not be saved during normal backups.  NO +
                          OPERATOR ACTION OR INTERVENTION IS +
                          REQUIRED.  This job will re-create the +
                          required UPS *MSGQ automatically.') +
                          TOMSGQ(QSYSOPR)
/**/
             CRTMSGQ    MSGQ(&UPSLIB/&UPSMSGQ) TEXT('Uninterruptible +
                          Power Supply Monitor Message Queue') +
                          SIZE(12) AUT(*EXCLUDE) /* Re-Create UPS +
                          Message Queue. */
/**/
             CHGOBJOWN  OBJ(&UPSLIB/&UPSMSGQ) OBJTYPE(*MSGQ) +
                          NEWOWN(QSECOFR) /* Force Owner Of Message +
                          Queue To Be QSECOFR. */
/**/
             ENDDO      /* If The UPS Message Queue Is Not Found, +
                          Create A New One, Change The Object Owner +
                          To MCCSYSCTL, And Warn System Operator Of +
                          This Condition.  Program Will Continue To +
                          Execute. */
/**/
/*********************************************************************/
/**/
 ALLOC_MSGQ:
/**/
             ALCOBJ     OBJ((&UPSLIB/&UPSMSGQ *MSGQ *EXCL)) WAIT(2) +
                          /* Attempt To Exclusively Allocate UPS +
                          Monitor Message Queue. */
             MONMSG     MSGID(CPF1002) EXEC(DO)
/**/
             SNDPGMMSG  MSG('WARNING -- Job ' || &JOBNUMBER |< '/' || +
                          &USER |< '/' || &JOB |< ' is unable to +
                          exclusively allocate Uninterruptible Power +
                          Supply *MSGQ ' || &UPSLIB |< '/' || +
                          &UPSMSGQ |< '.  This condition is caused +
                          when a second UPS monitor job has been +
                          started.  Only 1 UPS monitor job is +
                          permitted to execute.  This job will be +
                          ended (normally) automatically.  NO +
                          OPERATOR ACTION OR INTERVENTION IS +
                          REQUIRED.  If message re-occurs, eliminate +
                          cause of second UPS monitor job +
                          submission.') TOMSGQ(QSYSOPR)
             GOTO       CMDLBL(END)
             ENDDO      /* If UPS Monitor Message Queue Cannot Be +
                          Allocated, Advise System Operator And End +
                          The Duplicate Job. */
/**/
/*********************************************************************/
/**/
 MON_UPS:
/**/
             CHGVAR     VAR(&MSGID) VALUE('       ') /* Initialize +
                          This Variable. */
             CHGVAR     VAR(&TENSECOUNT) VALUE(0) /* Initialize The +
                          Ten Second Power Failure Loop Counter. */
/**/
             RCVMSG     MSGQ(&UPSLIB/&UPSMSGQ) WAIT(300) +
                          MSGID(&MSGID) /* Attempt To Receive Any UPS +
                          Related Messages. */
/**/
             IF         COND(&MSGID = 'CPF1816') THEN(GOTO +
                          CMDLBL(PWR_FAILED)) /* If Utility Power Has +
                          Been Lost, Jump To Power Failed Loop +
                          Section Of Program. */
/**/
             RTVJOBA    ENDSTS(&JOBCNLREQ) /* Retrieve Job Attribute +
                          Regarding Job Cancel Status. */
/**/
             IF         COND(&JOBCNLREQ = '1') THEN(DO)
             SNDPGMMSG  MSG('WARNING -- Job ' || &JOBNUMBER |< '/' || +
                          &USER |< '/' || &JOB |< ' is currently in +
                          cancel status.  The Uninterruptible Power +
                          Supply monitor program has been cancelled +
                          by another job or by the system operator.  +
                          View the system operator message queue for +
                          additional information.  This job will be +
                          ended (normally) automatically.  NO +
                          OPERATOR ACTION OR INTERVENTION IS +
                          REQUIRED.  UPS monitor job should be +
                          restarted as soon as possible.') +
                          TOMSGQ(QSYSOPR)
             GOTO       CMDLBL(END)
             ENDDO      /* If UPS Monitor Job Has Been Cancelled, +
                          Advise System Operator And End This Job +
                          Immediately. */
/**/
             IF         COND(&MSGID ¬= '       ') THEN(DO)
             CHGVAR     VAR(&LOOP_LABEL) VALUE('MON_UPS   ')
             GOTO       CMDLBL(OTHER_MSGS)
             ENDDO      /* If Other Messages Have Been Received, Set +
                          Return Loop Label, And Goto Other Messages +
                          Section Of Program. */
/**/
             GOTO       CMDLBL(MON_UPS) /* If Message ID Is Blank, +
                          Continue To Monitor UPS Power. */
/**/
/*********************************************************************/
/**/
 PWR_FAILED:
/**/
 NEXT_MSG:
/**/
             CHGVAR     VAR(&MSGID) VALUE('       ') /* Initialize +
                          This Variable. */
             CHGVAR     VAR(&TENSECOUNT) VALUE(&TENSECOUNT + 1) /* +
                          Increment Ten Second Power Failure Loop +
                          Counter. */
/**/
             RCVMSG     MSGQ(&UPSLIB/&UPSMSGQ) WAIT(10) MSGID(&MSGID) +
                          /* Attempt To Receive Any UPS Related +
                          Messages. */
/**/
             IF         COND(&MSGID = 'CPF1817') THEN(DO)
/**/
             IF         COND(&TENSECOUNT > 1) THEN(DO)
             SNDBRKMSG  MSG('ATTENTION ALL USERS  --  Electrical +
                          power to the computer room has been +
                          RESTORED.  You may continue to use the +
                          computer system at this time.  Additional +
                          messages will be sent if electrical power +
                          is lost again.  Contact ' || &MCCCUSMSG +
                          |< ' if you have any questions.') +
                          TOMSGQ(*ALLWS) /* Advise Users Of Power +
                          Restoration. */
             ENDDO      /* If Previous Message Has Been Sent +
                          Advising Users That Power Has Failed, Now +
                          Send Message That Power Has Been Restored. */
/**/
             GOTO       CMDLBL(MON_UPS)
             ENDDO      /* If Utility Power Has Been Restored, Advise +
                          Users Of Power Restoration, And Jump To The +
                          Monitor UPS Loop Section Of Program. */
/**/
             IF         COND(&TENSECOUNT = 1) THEN(DO)
             SNDBRKMSG  MSG('ATTENTION ALL USERS  --  Electrical +
                          power to the computer room has been +
                          LOST.  Unless power is restored within +
                          the next ' || &AWAITSEC || ' seconds, +
                          this computer will automatically begin to +
                          shut down.  PLEASE CANCEL YOUR CURRENT +
                          TRANSACTION AND PROCEED BACK TO YOUR MAIN +
                          MENU.  If utility power is restored in ' +
                          || &AWAITSEC || ' seconds, a message will +
                          be sent advising you that the system is +
                          now available for use.  Otherwise, +
                          contact ' || &MCCCUSMSG |< ' for +
                          assistance.') TOMSGQ(*ALLWS) /* Warn +
                          Users Of Power Failure. */
             ENDDO
/**/
             IF         COND(&MSGID ¬= '       ') THEN(DO)
             CHGVAR     VAR(&LOOP_LABEL) VALUE('NEXT_MSG  ')
             GOTO       CMDLBL(OTHER_MSGS)
             ENDDO      /* If Other Messages Have Been Received, Set +
                          Return Loop Label, And Goto Other Messages +
                          Section Of Program. */
/**/
             IF         COND(&TENSECOUNT < &WAITCYCLES) THEN(GOTO +
                          CMDLBL(NEXT_MSG)) /* If System Has Not +
                          Waited For Required Cycles (At Ten Seconds +
                          Each), Force Another Loop.  Once Required +
                          Cycles Has Been Completed, And Utility +
                          Power Restored Message Has NOT Been +
                          Received, Proceed With Next Step To Power +
                          Down System. */
/**/
 POWER_DOWN:
/**/
        QSYS/PWRDWNSYS  OPTION(*IMMED) /* Since Utility Power Has Not +
                          Been Restored, Power Down System +
                          Immediately.  Since System Is On UPS Power, +
                          A "Quick Power Down" Process Will Be +
                          Initiated. */
/**/
/*********************************************************************/
/**/
 OTHER_MSGS:
/**/
             IF         COND(&MSGID = 'CPF1816') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          ANOTHER CPF1816 indicating utility power +
                          has failed.  Receiving this message again +
                          without a subsequent CPF1817 (utility power +
                          restored) may indicate a problem exists +
                          with the UPS, the UPS attachment, or +
                          possible internal processing routines.  +
                          This potential problem should be +
                          investigated.  NO OPERATOR ACTION OR +
                          INTERVENTION IS REQUIRED.  UPS monitor job +
                          will continue running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPF1817') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          ANOTHER CPF1817 indicating utility power +
                          has restored.  Receiving this message again +
                          without a subsequent CPF1816 (utility power +
                          failed) may indicate a problem exists with +
                          the UPS, the UPS attachment, or possible +
                          internal processing routines.  This +
                          potential problem should be investigated.  +
                          NO OPERATOR ACTION OR INTERVENTION IS +
                          REQUIRED.  UPS monitor job will continue +
                          running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0961') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0961 indicating the Uninterruptible +
                          Power Supply (UPS) has been taken off-line +
                          and is no longer attached to system.  If +
                          utility power should fail, the system will +
                          not be protected.  If this is not a true or +
                          known condition, the situation must be +
                          investigated and corrected.  UPS monitor +
                          job will continue running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0962') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0962 indicating the Uninterruptible +
                          Power Supply (UPS) has been put on-line and +
                          is attached to system.  If utility power +
                          should fail, the system will be protected.  +
                          If this is not a true or known condition, +
                          the situation must be investigated and +
                          corrected.  UPS monitor job will continue +
                          running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0963') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0963 indicating the Uninterruptible +
                          Power Supply (UPS) is currently supplying +
                          system power.  If this is not a true or +
                          known condition, the situation must be +
                          investigated and corrected.  UPS monitor +
                          job will continue running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0964') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0964 indicating the Uninterruptible +
                          Power Supply (UPS) has a weak battery +
                          condition.  If the system loses utility +
                          power, the UPS monitor will release control +
                          of the processing.  The system will perform +
                          an immediate power down.  If this is not a +
                          true or known condition, the situation must +
                          be investigated and corrected.  UPS monitor +
                          job will continue running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0965') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0965 indicating a hardware problem in +
                          the model B10 or B20 UPS features.  If this +
                          is not a true or known condition, the +
                          situation must be investigated and +
                          corrected.  UPS monitor job will continue +
                          running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0966') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0966 indicating a hardware problem in +
                          the model B10 or B20 UPS features.  If this +
                          is not a true or known condition, the +
                          situation must be investigated and +
                          corrected.  UPS monitor job will continue +
                          running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0973') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0964 indicating the Uninterruptible +
                          Power Supply (UPS) no longer has a weak +
                          battery condition.  If the system loses +
                          utility power, the UPS monitor will control +
                          processing.  The system will not perform an +
                          immediate power down.  If this is not a +
                          true or known condition, the situation must +
                          be investigated and corrected.  UPS monitor +
                          job will continue running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0974') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0974 indicating the Uninterruptible +
                          Power Supply (UPS) has been taken off-line +
                          and is no longer attached to system.  If +
                          utility power should fail, the system will +
                          not be protected.  If this is not a true or +
                          known condition, the situation must be +
                          investigated and corrected.  UPS monitor +
                          job will continue running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0975') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0975 indicating the Uninterruptible +
                          Power Supply (UPS) has been put on-line and +
                          is attached to system.  If utility power +
                          should fail, the system will be protected.  +
                          If this is not a true or known condition, +
                          the situation must be investigated and +
                          corrected.  UPS monitor job will continue +
                          running.') TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0976') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0976 indicating the Uninterruptible +
                          Power Supply (UPS) monitor could not send a +
                          message to the UPS message queue.  If this +
                          is true, how was this message ever +
                          received?.  There is definitely a problem.  +
                          UPS monitor job will continue running.') +
                          TOMSGQ(QSYSOPR))
/**/
             IF         COND(&MSGID = 'CPI0981') THEN(SNDPGMMSG +
                          MSG('WARNING -- Job ' || &JOBNUMBER |< '/' +
                          || &USER |< '/' || &JOB |< ' has received +
                          CPI0981 indicating the Automatic IPL system +
                          value (QPWRRSTIPL) has been disabled.  +
                          Refer to prior messages in system operator +
                          message queue for additional information.  +
                          UPS monitor job will continue running.') +
                          TOMSGQ(QSYSOPR))
/**/
/**********/
/**/
             IF         COND(&LOOP_LABEL = 'MON_UPS   ') THEN(GOTO +
                          CMDLBL(MON_UPS)) /* If Loop Label Return +
                          Point Is MON_UPS, Then Return There To +
                          Monitor For Additional Messages. */
/**/
             ELSE       CMD(IF COND(&LOOP_LABEL = 'NEXT_MSG  ') +
                          THEN(GOTO CMDLBL(NEXT_MSG))) /* If Loop +
                          Label Return Point Is NEXT_MSG, Then Return +
                          There To Monitor For Additional Messages. */
/**/
             ELSE       CMD(DO)
             SNDPGMMSG  MSG('WARNING -- Job ' || &JOBNUMBER |< '/' || +
                          &USER |< '/' || &JOB |< ' is operating +
                          improperly.  The Uninterruptible Power +
                          Supply monitor program is processing "other +
                          UPS related messages" and has requested a +
                          loop label return point which does not +
                          exist.  Value in field LOOP_LABEL is ' || +
                          &LOOP_LABEL |< '.  Advise programmer of +
                          this problem immediately.  NO OPERATOR +
                          INTERVENTION IS REQUIRED.  UPS monitor job +
                          will continue running at MON_UPS loop label +
                          return point, but may operate +
                          incorrectly.') TOMSGQ(QSYSOPR)
             GOTO       CMDLBL(MON_UPS)
             ENDDO      /* If An Unknown Loop Label Return Point Has +
                          Been Identified, Advise System Operator, +
                          And Continue Processing Normally. */
/**/
/*********************************************************************/
/**/
 END:
/**/
ENDPGM





> 
> ----- Original Message -----
> From: "William Washington III" <w.washington3@xxxxxxxxxxxxx>
> To: "Midrange" <midrange-l@xxxxxxxxxxxx>
> Sent: Friday, February 20, 2004 11:32 PM
> Subject: Shutdown programs when UPS starts
> 
> 
>> Hello All,
>> 
>> Does the iSeries have a system value that holds the name of a
>> program to 
> run for certain events, like a UPS startup?
>> 
>> I'd like to shut down my iSeries in an orderly manner when the USP is
> activated, but I cannot find a "hook" to start my program.
>> 
>> It's kind of like my STARTUP program when I restart (IPL) my
>> machine.  I 
> have everything I want to start there... I wonder if the reverse
> functionality is there.
>> 
>> If it doesn't exist, can monitoring the QUPSMSGQ work?  Other ideas?
>> Thanks! 



As an Amazon Associate we earn from qualifying purchases.

This thread ...

Replies:

Follow On AppleNews
Return to Archive home page | Return to MIDRANGE.COM home page

This mailing list archive is Copyright 1997-2024 by midrange.com and David Gibbs as a compilation work. Use of the archive is restricted to research of a business or technical nature. Any other uses are prohibited. Full details are available on our policy page. If you have questions about this, please contact [javascript protected email address].

Operating expenses for this site are earned using the Amazon Associate program and Google Adsense.