If the supplies are billed as redundant that Must mean that each can do all the work if required and without any action by the user. Either of them can suddenly be the only one working but the system stays up.
In the case described here the supplies each carry roughly 50% of the load so the outlet and the UPS each get half. If the outlet goes dark then only the UPS remains to supply both it's current 50% plus the outlet's 50%. When there isn't that much headroom on the UPS then the UPS shuts off in self protection.
- Larry ChadB@xxxxxxxxxxxxxxxxxxxx wrote:
You're talking about splitting the cords between utility and UPS, and not about the reduntant power supply, right?*WARNING* *WARNING* *WARNING* In this configuration you *MUST* be certain that the UPS is never over 50% load! If it's at even 51% when the power fails and the UPS must carry all of the load instead of only half it caries now it will drop like a stone leaving you completely unprotected and of course unpowered as well!!. The only way to test this for sure is to unplug all the power supplies that go into the wall and see if the UPS can stand it! - Larry Chris Bipes wrote:
As an Amazon Associate we earn from qualifying purchases.
This mailing list archive is Copyright 1997-2024 by midrange.com and David Gibbs as a compilation work. Use of the archive is restricted to research of a business or technical nature. Any other uses are prohibited. Full details are available on our policy page. If you have questions about this, please contact [javascript protected email address].