Good data centers strictly enforce Hot aisle Cold aisle. Then they also
verify air flow on switches and routers etc move in the correct
direction and that all spaces are filled. If some stuff blows heat
forward and other rearward that can create a 'heat loop' that then
overheats both pieces.
We see many rooms where fans are running blowing air all over. Mostly
this is bad because it simply homogenizes the air mixing the hot and the
cold. Thus the available air to cool the servers is warmer than it could
be and the air going to the CRAC is cooler than it could be. Thus heat
removal is not as effective as it could be.
For facilities with raised floor it's important to remove old tapes,
manuals, cables and other 'crud' from below the floor. Also plug holes
that allow cold air to escape where it should not with pillows or
brushes. Place vented tiles where it will direct the cool air to the
Front (INTAKE side) of the equipment. Do not allow ANY cold air to reach
the outlet (hot) side of the racks. Remember the goal is not to put cold
in, it's to get HOT(Heat) out. If possible place return air ducts above
the hot side of the racks allowing the hottest air to get to the CRAC.
It's pretty amazing how much more efficient CRAC is when air-flow is
proper!
The 'magic heat gun' looks so awesome that I already ordered one. :-)
- Larry "DrFranken" Bolhuis
www.frankeni.com
www.iDevCloud.com
www.iInTheCloud.com
On 1/30/2014 9:15 AM, rob@xxxxxxxxx wrote:
Man, one of those laser temperature guns like below:http://www.harborfreight.com/non-contact-infrared-thermometer-with-laser-targeting-69465-8905.html
Really shows you where your computer room hot spots are.--
I really think it would be more efficient if we ducted our racks.
I should probably also be concerned that the breaker boxes on the loading
dock shows a few breakers well over 80o when the ambient temperature
surrounding them is under 60o.
These breakers control HVAC units on the roof. Another concern about
these is that when they blow they don't blow their individual breaker.
They blow the breaker which feeds their breaker box. Which also happens
to feed our computer room UPS. See my concern?
This breaker is a special one you will never see in a home application.
Rob Berendt
This is the Midrange Systems Technical Discussion (MIDRANGE-L) mailing list
To post a message email: MIDRANGE-L@xxxxxxxxxxxx
To subscribe, unsubscribe, or change list options,
visit: http://lists.midrange.com/mailman/listinfo/midrange-l
or email: MIDRANGE-L-request@xxxxxxxxxxxx
Before posting, please take a moment to review the archives
at http://archive.midrange.com/midrange-l.
As an Amazon Associate we earn from qualifying purchases.
This mailing list archive is Copyright 1997-2024 by midrange.com and David Gibbs as a compilation work. Use of the archive is restricted to research of a business or technical nature. Any other uses are prohibited. Full details are available on our policy page. If you have questions about this, please contact [javascript protected email address].
Operating expenses for this site are earned using the Amazon Associate program and Google Adsense.